Default (new garage & pouring floor) need concrete specs for 2 post lift?

I am building a garage and I want to install a 7K 2 post lift. I need to pour the floor but I am unsure what thickness and p.s.i. concrete I will need?

What size area around the posts?
9t8z28 is offline   Reply With Quote
Old 04-12-2009, 09:15 PM   #2
TECH Enthusiast
iTrader: (8)
 
vaticano's Avatar
 
Join Date: Feb 2006
Location: Denver Colo.
Posts: 532
Default

A 4 inch slab will be sufficient. Most garages are 4", but you can go deeper if you like. Just thicken the areas under the posts to 8-12 inches deep, and 2 foot square, put 4, 4ft pieces of rebar, #4 should be fine, bend them a bit so they go down into the thickened areas. You want 2 each way centerd on the hole. A standard 6 sack 4000 psi mix will be fine. Just don't let whoever pours it, add to much water, it will weaken the concrete. You want a 4 inch slump. You should also put some wire mesh or rebar in the slab itself. This will hold it together when it cracks. Rebar is better but mesh is cheaper. If you use the mesh make sure to pull up so it is in the center of the slab. Also you will need to cut exspansion joints to control cracking and relieve the exspansive stresses. You should cut the joints so that you have 10'x10' sections. If you need more info let me know.
vaticano is offline   Reply With Quote
Old 04-12-2009, 09:43 PM   #3
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Quote:
Originally Posted by vaticano View Post
A 4 inch slab will be sufficient. Most garages are 4", but you can go deeper if you like. Just thicken the areas under the posts to 8-12 inches deep, and 2 foot square, put 4, 4ft pieces of rebar, #4 should be fine, bend them a bit so they go down into the thickened areas. You want 2 each way centerd on the hole. A standard 6 sack 4000 psi mix will be fine. Just don't let whoever pours it, add to much water, it will weaken the concrete. You want a 4 inch slump. You should also put some wire mesh or rebar in the slab itself. This will hold it together when it cracks. Rebar is better but mesh is cheaper. If you use the mesh make sure to pull up so it is in the center of the slab. Also you will need to cut exspansion joints to control cracking and relieve the exspansive stresses. You should cut the joints so that you have 10'x10' sections. If you need more info let me know.
How deep should the rebar be if say I make the 2 foot square section under the posts 6" ?

When you say "4" slump", what do you mean?

Thanks for the info in detail
9t8z28 is offline   Reply With Quote
Old 04-12-2009, 09:59 PM   #4
TECH Enthusiast
iTrader: (8)
 
vaticano's Avatar
 
Join Date: Feb 2006
Location: Denver Colo.
Posts: 532
Default

Quote:
Originally Posted by 9t8z28 View Post
How deep should the rebar be if say I make the 2 foot square section under the posts 6" ?

When you say "4" slump", what do you mean?

Thanks for the info in detail
The rebar should be just above the bottom of the fasteners you are using to hold the lift posts. So if the fasteners are 4" into the floor, you want the rebar at 3" down.

Concrete is tested with a slump test. What this means is a tester will take a 1 foot cone and fill it with concrete, consolodate it with a rod by poking it, the cone is then removed and a measurement is taken from the from the top of the cone to the top of the concrete. That # in inches will be the slump. When you order it just tell the batch plant you want a 4 inch slump, then when the driver gets there tell him the same. They will get you close. Plus or minus an inch wont hurt, but I have seen people pour out concrete that flows like water. This is not good and will cause failure.

If you are doing this your self, make sure you have all the tools to finish it. Finishing is what you do to the surface to smooth it out.
vaticano is offline   Reply With Quote
Old 04-12-2009, 10:03 PM   #5
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Quote:
Originally Posted by vaticano View Post
The rebar should be just above the bottom of the fasteners you are using to hold the lift posts. So if the fasteners are 4" into the floor, you want the rebar at 3" down.

Concrete is tested with a slump test. What this means is a tester will take a 1 foot cone and fill it with concrete, consolodate it with a rod by poking it, the cone is then removed and a measurement is taken from the from the top of the cone to the top of the concrete. That # in inches will be the slump. When you order it just tell the batch plant you want a 4 inch slump, then when the driver gets there tell him the same. They will get you close. Plus or minus an inch wont hurt, but I have seen people pour out concrete that flows like water. This is not good and will cause failure.

If you are doing this your self, make sure you have all the tools to finish it. Finishing is what you do to the surface to smooth it out.
Wow. Awesome info.

Thanks
9t8z28 is offline   Reply With Quote
Old 04-14-2009, 01:33 PM   #6
TECH Senior Member
iTrader: (90)
 
01ssreda4's Avatar
 
Join Date: Aug 2007
Location: Turnin' Wrenches Infractions: 005
Posts: 21,361
Default

wow i know who to ask advice from on my concrete project....
01ssreda4 is offline   Reply With Quote
Old 04-14-2009, 02:57 PM   #7
TECH Addict
iTrader: (41)
 
Bad Blue WS6's Avatar
 
Join Date: Feb 2006
Location: Germantown Hills IL
Posts: 2,003
Default

that is some good stuff.
Bad Blue WS6 is offline   Reply With Quote
Old 04-14-2009, 03:45 PM   #8
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

What is the difference from pouring it in one shot (footer and floor) vs. pouring the footer, letting it dry and then pouring the floor?

Someone mentioned to me (mono-lithick).? What does this mean?
9t8z28 is offline   Reply With Quote
Old 04-14-2009, 07:48 PM   #9
TECH Enthusiast
iTrader: (8)
 
vaticano's Avatar
 
Join Date: Feb 2006
Location: Denver Colo.
Posts: 532
Default

Monolithic is just as you explained, Pouring the 2 pieces as one.

A footing or footer is nothing more than a stable block for a wall to sit on. It will help to spread the weight of the wall over a larger area to prevent sinking, while stablizing the wall from falling over.

The wall will be centered on the footing with 1 foot of concrete on each side of the wall. So if you had an 8" thick wall the footing would be 2' 8" wide, for residential walls, 12" deep. This will vary depending the what the wall will be used for and it's size.

Pouring a footing and a wall at same time is very dificult for several reasons.

With a footing you have a solid surface to build the wall forms on.
Without the footing you would have suspend the wall forms in the air.

(Could you imagine the trouble you would have holding a 30' long 8' high wall of plywwod in the air. And that would be just 1 side. If this was a house you would have 4 of these all together.)

This does not provide for a stable form. the form can easily move laterally making it hard to keep it straight.

You have vibrate concrete to prevent large holes in a wall.
This vibration causes the concrete to flow or move very easily.

Doing this monlithic would cause most of the concrete to move from the wall and overflow out of the footing.

You could put a lid on the footing, but the lid would allow for alot of trapped air and prevent the footing from filling properly.

It is alot easier to pour these types of things in 2 pours.
There are a few exceptions to this, but not many.


If any of you guys have any questions feel free to ask. I will answer them the best I can.

Just a little extra info.
Here is the formula for figuring how much concrete you need to fill a space.

Legnth X Width X Height / 27 = Cubic Yards

That will be the # you need to order it from the batch plant.
vaticano is offline   Reply With Quote
Old 04-14-2009, 08:46 PM   #10
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Once again, you have helped alot. I am trying to rap up the plans and get the ball moving.

Thanks
9t8z28 is offline   Reply With Quote
Old 04-14-2009, 09:02 PM   #11
TECH Enthusiast
iTrader: (8)
 
vaticano's Avatar
 
Join Date: Feb 2006
Location: Denver Colo.
Posts: 532
Default

No problem.
vaticano is offline   Reply With Quote
Old 04-20-2009, 07:53 PM   #12
TECH Enthusiast
iTrader: (8)
 
SSJIMMY's Avatar
 
Join Date: May 2005
Location: Sanford, FL
Posts: 506
Default

I think 4" is considered the minimum but I would say 6" shoud be the minimum but follow vaticano suggestions cause you cant have to much support for a lift.

post some pictures up once you get the slab poured and the framing started.
SSJIMMY is offline   Reply With Quote
Old 04-20-2009, 07:59 PM   #13
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Quote:
Originally Posted by SSJIMMY View Post
I think 4" is considered the minimum but I would say 6" shoud be the minimum but follow vaticano suggestions cause you cant have to much support for a lift.

post some pictures up once you get the slab poured and the framing started.
I will. Hopefully it stops raining!
9t8z28 is offline   Reply With Quote
Old 04-20-2009, 08:33 PM   #14
TECH Enthusiast
iTrader: (8)
 
SSJIMMY's Avatar
 
Join Date: May 2005
Location: Sanford, FL
Posts: 506
Default

Send some of that rain down here we could use it to get rid of some of the fires.

whats some of the specs on the shop your building.
SSJIMMY is offline   Reply With Quote
Old 04-20-2009, 09:49 PM   #15
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Quote:
Originally Posted by SSJIMMY View Post
Send some of that rain down here we could use it to get rid of some of the fires.

whats some of the specs on the shop your building.
It was going to be 20 x 30 but that just wouldn't cut it. I have an Impala that is over 18 FOOT long and I wouldn't be able to manuver it around (on coasters) along with my Chevelle being in there. We are going to increase the length by 15' and that will be enough for all of my tool boxes and engine blocks. The ceiling is 16' in the center. Next week I am going on the road to go and pick up my 9K Rotary lift that I scored for $800 !!!
9t8z28 is offline   Reply With Quote
Old 04-21-2009, 08:10 AM   #16
Teching In
iTrader: (3)
 
Join Date: Mar 2009
Location: Carlisle, PA
Posts: 9
Default

Nice price on the lift. I have seen 7K units for over $1400. Most of the 7K units I was looking at called for min of 4" 3000 PSI concrete. So I poured 6" in that area and dug 2 24" round by 36" deep pillars and poured them along with the floor. Now my lift posts will sit right on these pillars. Super easy to do when you have an auger on a skid loader. Do yourself a favor, coat the garage floor with some epoxy while it is still new. I did mine with epoxy-coat and it came out great.
cresswellracing is offline   Reply With Quote
Old 04-21-2009, 03:50 PM   #17
7 Second Club
iTrader: (11)
 
Phil99vette's Avatar
 
Join Date: Jul 2002
Location: Port Tobacco, MD
Posts: 8,751
Default

4" with rebar is enough, 6" is what I did with rebar.
Phil99vette is offline   Reply With Quote
Old 04-21-2009, 07:14 PM   #18
11 Second Club
Thread Starter
iTrader: (19)
 
9t8z28's Avatar
 
Join Date: Jan 2007
Location: Doylestown, Pa
Posts: 1,350
Default

Quote:
Originally Posted by Phil99vette View Post
4" with rebar is enough, 6" is what I did with rebar.
4" with a 9K lift?
9t8z28 is offline   Reply With Quote
Old 04-21-2009, 08:09 PM   #19
7 Second Club
iTrader: (11)
 
Phil99vette's Avatar
 
Join Date: Jul 2002
Location: Port Tobacco, MD
Posts: 8,751
Default

I ordered a Challenger VS10 lift, its symetric and asymetric if needed. It requires a 4" slab with rebar, I chose to do 6". Its a 10k lift. Check out...
http://www.challengerlifts.com/VS10.shtml
Phil99vette is offline   Reply With Quote
Old 04-21-2009, 08:10 PM   #20
7 Second Club
iTrader: (11)
 
Phil99vette's Avatar
 
Join Date: Jul 2002
Location: Port Tobacco, MD
Posts: 8,751
Default

The lift was 2600 installed, more than the greg smith but I'm still not sold on a the cheap lifts, lets face it.... If the lift comes down you could lose your life
Phil99vette is offline   Reply With Quote
Reply

Related Topics
Thread Thread Starter Forum Replies Last Post
Bridges & Engineering Need4Camaro Racer's Lounge 35 04-10-2015 04:05 PM
Looking to start up a dyno business. Need help! oddwraith Tools & Fabrication 34 07-19-2014 08:50 PM
Garage lift- Who has one Blackfly Texas Members 14 11-09-2010 06:58 AM
Who has installed a 2-post lift on a residential slab? SS14PSI Tools & Fabrication 18 07-10-2010 10:11 PM
2 post lifts in a home garage Dip Stick Tools & Fabrication 19 06-11-2007 05:04 AM


Tags
cement, codes, concrete, floor, garage, inch, lift, post, pour, pouring, quote, rotary, side, slump, specifications, specs

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are Off



All times are GMT -5. The time now is 03:46 PM.