Welder extension cord question
dryer plug
L L
red\ black/ or black\ red/
does it matter?
Also, in my panel the grounds and neutrals share two sides of the panel. If the welder uses a ground, then when I attach the extension cord ground to the outlet, will it be grounded or energized with the neutral? I suspect it will be okay.
Last edited by shep28; Aug 13, 2009 at 12:27 AM. Reason: info
The 2 hot wires don`t matter as far as order. they each carry 120v between them and ground/neutral, or if you measure between them its 240v because they are on opposite phases.
In theory ground and neutral are different, in common household practice they are essentially the same. In the panel there should be a ground bar and a seperate neutral bar. The ground bar ties all the grounds together and then to a ground rod/water pipe. The neutral ties all of the neutrals together and to the neutral line coming in, and also through the pipe/panel it is tied to the ground bar. If your welder has 3 wires coming out of it it is the standard 2 hot wires and a neutral. If it is a newer welder it may have 4 wires, which would be 2 hots, a neutral and a ground, which would mean you should be using a 4 wire cord/plug.