Who knows electrical?
1) Do I run a ground wire off the garage panel to a ground rod outside? If so what size should that wire be?
2)How many outlets can I safely put on a 20 amp breaker without tripping it all the time?
3)Do I make the first outlet in every circuit a GFI or does every outlet have to be a GFI
Thanks in advance,
Bryan
Last edited by UA-Plumber; Oct 31, 2006 at 05:58 PM.
1) Do I run a ground wire off the garage panel to a ground rod outside? If so what size should that wire be? Not sure, but run to a ground rod at the garage. Rule of thumb is, whatever ga. wire you bring in, run the same for a ground.
2)How many outlets can I safely put on a 20 amp breaker without tripping it all the time? Between 4 and 6 safely.
3)Do I make the first outlet in every circuit a GFI or does every outlet have to be a GFI The first one should sufice, but I like to do every other.
Thanks in advance,
Bryan
Hope that helps.
Trending Topics
1) Do I run a ground wire off the garage panel to a ground rod outside? If so what size should that wire be? Run a green or bare ground wire from a ground rod to the sub panel. Use a #4 copper wire for 100 amps.
2)How many outlets can I safely put on a 20 amp breaker without tripping it all the time? Only one outlet per breaker if you have something like an air compressor or heater that draws 15 amps or more. Plan ahead and have a separate circuit on each side of your workbench as well. I suggest no more than 6 outlets per breaker if they will only be used for lights, radio etc. Running more circuits with fewer outlets on each is always better than not enough circuits. You are not limited to only 3-20 amp breakers on your 60 amp main panel as you might think. Buy a sub panel with plenty of spaces and don't forget to allow for at least 4 spaces for a couple of 240 volt breakers (mig welder, air compressor, powder paint oven etc).
3)Do I make the first outlet in every circuit a GFI or does every outlet have to be a GFI? Just the first outlet on each circuit as long as you wire it for pass through protection to the other receptacles on that same circuit (use all 4 GFI terminals plus ground).
Last edited by gto69judge; Dec 29, 2006 at 12:40 PM.
The Best V8 Stories One Small Block at Time
you should (really really) run at least a 8 gauge ground to the panel.
code in the n.e.c. book is 10 outlets per circuit.10 lights per circuit.
only the home run for the plugs needs to be gfi, if any plug trips it will just trip the gfi(and u dont have to walk 75 feet to turn the breaker back on.
i've done close to 10 same size garages and no complaints(just make sure your panel can handle everything)i would use a sub panel
you should (really really) run at least a 8 gauge ground to the panel.
code in the n.e.c. book is 10 outlets per circuit.10 lights per circuit.
only the home run for the plugs needs to be gfi, if any plug trips it will just trip the gfi(and u dont have to walk 75 feet to turn the breaker back on.
i've done close to 10 same size garages and no complaints(just make sure your panel can handle everything)i would use a sub panel
I agree that a sub panel is the best plan for your shop. Be sure NOT to connect the ground and neutral at your sub pannel. There is only one G-N connection allowed at the service entrance (your main pannel).
Some suggestions;
- Use 12 gauge wire for all your branch circuits.
- Install 2 gang boxes and put in 2 outlets each.
- Put the disconnect by the door. It's nice to turn all the shop off with a single switch. This eliminates the possibility of leaving something on and causing a fire.
Bryan
Last edited by gto69judge; Nov 26, 2006 at 01:15 PM.
If you anticipate a large garage draw (such as a 2 stage air compressor and large welder running simultaneously) you should run larger wire (such as #2 or better yet, #0 Aluminum) to the garage capable of supplying 100 amp service. That way, if you eventually upgrade your house panel, you can simply change out the 60 amp breaker for a 100 amp breaker.
Copper wire has doubled in price this summer so install a large conduit that will allow you to use the larger Aluminum wire instead of copper. Aluminum wire is used to feed your electric meter and probably your main panel and is fine for feeding your sub-panel. Use Copper wire for all your branch circuits inside your garage.
If you are running 12 guage 20 amp circuits, you should use 20 amp rated outlets. They are stronger which is useful for a garage, but they also will not overheat if you pull more than 15 amps through the outlet. Since the breaker and wire will allow the full 20 amps to pass.
I have two sub-panels and a 100 amp circuit that goes to the attic for a heat pump electrical heat elements all using aluminum with no problems. Just don't forget the paste.
If the main panel has a ground, you can run a ground through the conduit which would carry the ground to your sub-panel. If the conduit is large enough, just get an aluminum feeder cable in #2 or #0 wire and it will have all the wires and ground wrap necessary to properly connect the two boxes.
Good luck with your project!
First off, your garage will need a ground rod or concrete encased electrode-20' of rebar in the slab/footing is typical. Run a #4 cu. conductor from the sub's ground bar to this ground or encase 20' of #4 in the slab. The #4 cu.feeding your sub is good for 100 amps(depending on the insulation) so if you feel the need to up your house service to supply 100 amps to the shop later, you will be fine.
The NEC requires you to calculate each recp. at 180 volt amps (1.5 amps) and not exceed 80% of the overcurrant (breaker) device. If you are using # 12 this should work out to 10 recepticles per 20 amp breaker. This is the MAX number permitted but you should determine your loads and provide circuits as needed. A metal chop saw will draw 12+ amps so you would want it on its own circuit for instance.
Remember, you can only use one device at a time; welder, grinder, drill press, etc, with the added load of maybe your air compressor, lights and maybe a cooler of some kind. The 60 amps will go a long way in a moderate shop, especially if you are the only one using power tools there. If you properly size your overcurrant devices to your wire, you should have not worry of fire.
A GFCI installed in the first outlet of a circuit can be wired to GFCI all downstream outlets All 120 volt recepticles must be GFCI protected.
Most towns require permits and inspections and local ordinances may modify(or not even follow) the NEC so you need to check with your local Building Department.
BTW, I've been a member of the IBEW for 35 years, an electrical inspector for 17.