Shop wiring questions
). The shop is still a good 6 months away, but I am planning out all the details right now. At the moment I am designing the circuits for the wiring of the shop and I don't know how many amps to use for the welder. I was thinking 50 amps with 6-3 cable running to it at 220 V, but I didn't know if that is the standard or if 30 amps was. I know that I could just look at the input requirements of the welder, but I want to use the amperage that is commonly found in welder circuits.
Also, how many total amps are you guys getting away with running to your shops? Mine is only going to be a small 30' X 35' with minimal large amp power tools (welder, compressor, and table saw), so I am thinking 100 amps total. Does that sound right or should I go with more or less? I have calculated my consumption and came in right around 100-125 amps total (using 50 amps for the welder circuit), but that is with every light on and every circuit being used to its max capacity which I doubt will ever happen. Thanks in advance.
Victor
To find the approximate amperage of electrical devices use the Ohms Law formula, Amps = Watts divided by Volts. Example... A 1,200 watt device at 120 volts would be 10 amps.
My 24x40 became extremely small and is now 24 x54, and am looking at ways to expand even more.
I went with 150A service and wish I had gone 200A. The cost is negligible ...
I have 50A breakers for my welder and plasma cutter, 30A for my compressor.
Trending Topics
The Best V8 Stories One Small Block at Time
I say leave some space on the pad for a breezeway
and a generator alcove, in which to mount a nice
15kW diesel with electric start and a 25+ gallon tank.
Then consider how much power you want to be able
to run back to the house for emergency duty, that
size generator will serve any normal shop's needs
(yeah, who wants to be normal? Show of flippers?).
And running the genny regularly will be good for it.
The more country you are, the less the power company
prioritizes your service. Fastest restoration for the
most people and all that.
Compressor circuit - 20-30A
Welding circuit - 50a
HVAC - 30a
General lighting/receptacles - 20a
You may not use all major loads at once, but with 50 you may be selling yourself short. Yes, #6 is the correct wire for 50a.
#14 - 15a
#12 - 20a
#10 - 30a
#8 - 40a
#6 - 50a